Adding to an existing battery bank [RE-wrenches]
Tom Elliot, Guffey Energy Works
telliot at wagonmaker.com
Sun Jun 19 21:47:29 PDT 2005
<x-flowed>
The first suggestion I'd give you is, you guessed it coming from me, use a
buss bar. 4 strings won't present a problem if you do that. When you do
decide to put in a buss bar I don't see any need to break up the existing
strings because each individual string will contribute what it can and not
negatively impact the new strings.
Tom Elliot
----- Original Message -----
From: "Dan Rice" <danrice at scinternet.net>
To: <RE-wrenches at topica.com>
Sent: Sunday, June 19, 2005 5:07 PM
Subject: Adding to an existing battery bank [RE-wrenches]
>
> Esteemed Wrenches,
>
> Gubment job, to include doubling an existing, one year old battery bank of
> 8
> Trojan L-16 G's (two strings of four -24 VDC nominal system) -final
> configuration will be 4 strings of 4 (I recommended against doing
> this...).
> The site is an existing Nat'l Park Service administrative site, complete
> with 20 kW propane generator, stacked 4024's, and an 1800 Wp array. Mostly
> summer time use; mothballed during snow season. 5-6 kW-h/day use when
> occupied.
>
> Question: what would be the least potentially problematic battery bank
> reconfiguration? Should the existing strings be left intact, and the new
> batteries be installed in two strings? Or, should the existing strings be
> broken up, and made up into 4 new strings consisting of two old and two
> new
> batteries in each string? I'm inclined to do the latter, to balance the
> resistance of the parallel strings, but I'm not sure if that matters and
> if
> that might introduce another type of problem that I'm not aware of. As an
> aside, have others come across multiple string banks in which the cell
> closest to either the positive or negative end has deteriorated faster
> than
> the other cells? If the strings are broken up, should the new batteries be
> on the ends of the strings, leaving the year olds as the center two in
> each
> string? What is the failure mechanism that attends adding new batteries to
> old? Is it primarily related to uneven string currents causing accelerated
> and uneven wear?
>
> The Park Service is already aware that this battery bank configuration is
> not optimal, and is planning to upgrade to industrial batteries at the end
> of this set's life, but for now they need additional capacity and the
> existing battery set is only a year old. They're hoping to get 3-5 years
> out
> of this set.
>
> As always, your collective experience is much valued and appreciated.
>
> Dan Rice
> Abundant Sun, LLC.
> 435-826-4565
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list