Duh, here's the easiet way to eliminate the power draw of the controller for
remote start. Simply wire the remote start switch in parallel with the run
contacts of the Kohler on-board switch. Do not put the on-board switch in
the auto position. Leave it it the stop (middle) position. It will
start/stop just fine remotely and the starting battery will not drain down.
No need to remove the 48 hr power-down jumper either. No additional relays
required.
Vermont Solar Engineering
Kirk Herander
North American Board of Certified Energy Practitioners
Certified Solar PV Installer(TM)
Xantrex Certified Dealer Charter Member
NYSERDA-eligible installer
Vermont Solar and Wind Partner
PO Box 697
Burlington, VT. 05402
www.vermontsolar.com
www.backeastsolar.com
800.286.1252 - 802.863.1202
fax 802.863.7908
----- Original Message -----
From: "Kirk Herander" <kirk at vtsolar.com>
To: <RE-wrenches at topica.com>
Sent: Wednesday, December 01, 2004 6:03 PM
Subject: More Kohler RES controller stuff [RE-wrenches]
Hello Group,
Supposedly a fix to eliminate the power draw of the RES controller is in the
works at Kohler. I encourage any one who has experienced a dead starting
battery as a result of controller power drain to complain to your Kohler
rep. Perhaps that will encourage the factory to hustle on this one. I have
found out that these controllers were originally designed for some sort of
marine-based product they make, so it was not engineered for off-grid
applications (and not really utility backup either). Dumb thing is that the
controller's memory is captive, so no power is required when the generator
is off.
BTW, the RES operation manual states that this series is "approved for use
in backup situations where realible utility power is present". Unfortunately
Kohler is touting the RES as a direct replacement for the RMY series. An
irate customer pointed this out in the manual to me - so I had to verify
that the warranty is good in an off-grid situation - which it is.
Just another pain in the butt that our industry seems to abound in
sometimes, for which we have to find a work-around. A fix can be easily done
with a DPST 12vdc relay, but I haven't gotten Kohler to approve my wiring
diagram yet. The remote start (a switch) can energize the relay coil(powered
by the starting battery) and the respective contacts close to both provide
the remote start signal of the generator, and power to the controller. When
the remote switch opens, it disconnects controller power, thus killing the
phantom load.
Kirk
Vermont Solar Engineering
Kirk Herander
North American Board of Certified Energy Practitioners
Certified Solar PV Installer(TM)
Xantrex Certified Dealer Charter Member
NYSERDA-eligible installer
Vermont Solar and Wind Partner
PO Box 697
Burlington, VT. 05402
www.vermontsolar.com
www.backeastsolar.com
800.286.1252 - 802.863.1202
fax 802.863.7908
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
** Get Your Own Support-a-Cure Yellow Bracelet for $1.99 **
Show your support for finding cures for both AIDS & Cancer.
Get yours for just $1.99. This bracelet makes a difference.
http://click.topica.com/caacVlObz8Qcsbz9JC9f/Penn Media
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list