Colleagues:
I can't fault an inspector for red-tagging high voltage wiring running
along a ridge top, unprotected by conduit. This seems way too
dangerous. Roofing is abrasive, right? People walk on roofs, right? How
long until this wiring insulation wears through?
Just my humble opinion.
William Miller
At 06:04 PM 12/7/2004, you wrote:
>Wrenches: I recently had an inspector reject my use of USE-2 wire with
>MC connects on the array end as the primary wire coming from the array
>to the inside wiring . This was a roof-mounted grid- tie system and what
>I had done was ran from the array with a pair of USE conductors running
>along the roof peak, securely fastened, led over the side and led into a
>jbox immediently behind the siding up under the eave.From there I ran
>romex through the attic down to a Sunny Boy in the garage. He made me
>put the wires in flex conduit. I first showed him the UV rating on the
>wire but he wasnt going for it. Was I wrong to use it exposed in that
>application even though it was only running 10' along a second story
>rooftop?
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list