On the two dozen or so battery-ups installations I've done so far
I don't think an inspector has ever given a second thought to the
type of battery cable we've used, let alone the sizing. We almost
always use the orange-jacket Carol Super Vutron welding cable
which is very flexible, soft jacketed, UL listed-600 volts, easy to
handle, cost effective... and not JW approved. Using THHN in
battery cabinets would be problematic...and I don't think that
USE is really very much better. Remember that battery service
(water, testing) and replacement require access---shouldn't the
wire type be appropriate for that?

JW brings up some valid concerns with the terminations on
flexible cable, but using stiff cable also creates many problems.
Moreover, every RE system I've ever seen has significantly
oversized wiring anyway (usually sized for Vdrop vs thermal).

On this issue of wire type... it's good to remember that code is
interpreted--and enforced--at the local level. If you have a good
argument for a particular method, its often (usually?) possible
to get buy-in with the building officials.

/wk

At 09:20 AM 8/26/2004, you wrote:


>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Save up to 80% on Inkjet & Toner Supplies. 100% Satisfaction Guarantee. 
>Free Shipping on orders over $49. www.inksoutlet.com
>http://click.topica.com/caacAsfbz8Qcsbdh77Ha/Inksoutlet
>-------------------------------------------------------------------
>
>
>>Yet I often walk away from a job thinking that maybe I should have added
>>solder to the lug, to make it a permanent connection.
>>
>>
>>Kurt Nelson
>
>Just so Ya'll know, I cut open one of those spendy Trace inverter cables 
>that is totally UL etc.. It is only crimped. After that I have never given 
>a second thought about soldering again. Don't lose sleep Kurt.
>Also, I actually don't like the very fine stranded cables: welding cable, 
>Cobra, etc. Those little hairs going everywhere, and the crimps always 
>look like they're crushing down too far. On the coarse side, obviously 
>THHN is too stiff.
>I use (oh my god don't tell JW) I use SAE rated "Battery" cable from DC 
>wire. Its just the right combo of flex and coarse enough to work well in 
>the screw type lugs. Inspectors here have never questioned it. Who knows 
>battery cable better than the Society of Automotive Engineers?  JW, NEC, 
>UL, I don't think so.  And to get down to actual strand count, this SAE 
>stuff is 133 strands for 2/0, 418 strands for 4/0. Just about perfect 
>IMHO. BTW, when I order industrial 2 volt batteries, they come with this 
>same cable and the inspector can't argue with the manufacturer. Oh, but 
>none of the batteries are UL listed, so we're all screwed if the inspector 
>wants to get tough anyway.
>
>Ray
>Your free subscription is supported by today's sponsor:
>-------------------------------------------------------------------
>Stories from the Civil Rights Movement. Extraordinary stories, ordinary 
>people. Share your memories today!
>http://click.topica.com/caacvglbz8Qcsbdh77Hf/AARP
>-------------------------------------------------------------------
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
>
>
>
>
>---
>Incoming mail is certified Virus Free.
>Checked by AVG anti-virus system (http://www.grisoft.com).
>Version: 6.0.737 / Virus Database: 491 - Release Date: 8/11/2004

--
[Non-text portions of this message have been removed]

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Stories from the Civil Rights Movement. Extraordinary stories, 
ordinary people. Share your memories today!
http://click.topica.com/caacvglbz8Qcsbz9JC9f/AARP
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------



</x-flowed>



More information about the RE-wrenches mailing list