Allan Sindelar wrote:
> OK, so the above confuses me. If one of two inverter bypass switches is
> in bypass mode, that inverter's input and output are disconnected from
> both load and external source. While the neutral remains connected and
> common with the other inverter, there is no current supplied to that
> neutral conductor by the bypassed inverter. So if the inverter that is
> in normal mode references to an external AC source, and the bypassed AC
> leg uses that source to power loads (180 out of phase), where's the
> problem, at least in reference to overloading the neutral?
The scenario goes like this - the inverter's won't stay sync'd to a
generator - so the customer throws just one of the bypasses - resulting
in that leg of the 120/240 vac split phase system operating at the
generator's phasing. The other inverter does not sync to the generator
and operates on its own - unaware that the other inverter is not
following it anymore. The result is that the two AC legs can go in and
out of phase with each other - resulting in anything from zero to 240
vac applied to the L1-L2 and up to twice the current in the neutral
conductor. Usually the phasing goes in and out quickly - but I have
seen them stay phased in / out of phased for several minutes at a time,
slowly alternating between the two conditions. This also occurs when
the stacking cable of some inverters gets unplugged between the units -
and they don't shut down or show and error - they just keep operating on
their own...
We all have lived with these kinds of problems for years - but I think
this is one of those real-world, actually-does-happen type of problems
which should be addressed (as opposed to the theoretically-possible,
but-so-extremely-unlikely issues like islanding with a magically
balanced load condition that UL tends to focus on...)
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas @ outbackpower.com
www.outbackpower.com
Arlington WA USA
Tel 360 435 6030
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Sponsor a child today through Children International.
Give a desperately poor child hope for a brighter future.
For only $18 a month you can make a difference!
http://click.topica.com/caacpgsbz8Qcsbz9JC9f/ChildrenInternational
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list