I once had a system with repeated C30 failures in a frequent
lightning area. We had the array grounded separately from the C30.
i.e. there was a ground rod at the array, a ground rod at the SW but
no ground wire between. I've theorized that when lightning hit -
even a few miles away - a voltage difference develops between the two
rods and you blow the equipment. This was our theory anyway - when
we added a ground wire between the two rods the failures stopped.
You say the system was well grounded - how well?
Jeff C.
>
>Greetings all,
>
>I have a grid-tied System with battery that was installed in 1999 and
>has been glitch free since. The client came home after a weekend away
>and found no power in the residence. There had been a bad storm in the
>area while they were gone. The system was well grounded and had Deltas
>front and rear. In any case, they cycled power to the SW and it took
>right off with things apparently working normally.
>
>Since then, however, there has been a couple other storms in the area,
>and apparently all that needs to be present is a little rumble of
>thunder and the SW shuts down. Never happened like that it the past.
>Any thoughts greatly appreciated.
>
>Kurt Nelson
>
>===========================================================
>Buy Stocks and Index Funds for just $4 No Account or
>Investment Minimums and No Inactivity Fees Automatically
>invest weekly or monthly and build your future.
>http://click.topica.com/caaccMMbz8Qcsa9hBZif/ Sharebuilder
>===========================================================
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
>
>List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
--
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design Associates
http://www.villagepower.com
jeffc at villagepower.com
Sustainable Energy & Water Solutions for Home & Village
NABCEP Certified PV Installer
Office: (413) 256-6777, Cell: (720)480-8455
Fax: (413) 825-0372
61 Baker Road
Shutesbury, MA 01072;
PO Box 115
Boonville, CA 95415
(877) 765-2784
Council Member - Ecovillage Network of the Americas - http://www.ecovillage.org
Advisory Board - Living Routes - Ecovillage Education -
http://www.livingroutes.org
Founder: Ecovillage Research, Development, and Demonstration Program:
http://www.home.earthlink.net/~clrwater/RDD/rdd.html
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~
===========================================================
Domains as low as $4.95!
Limited Time! ICANN Accredited GoDaddy!
http://click.topica.com/caaccM5bz8Qcsbz9JC9f/ GoDaddy
===========================================================
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list