Geoff,

Sorry you missed the glove question... I was pulling the 8' from memory in
talking with inspectors, but here is what I have found in the code:

NEC 110.27.A

"...electrical equipment operating at 50 volts or
more shall be guarded against accidental contact by approved
enclosures or by any of the following means:
(1) By location in a room, vault, or similar enclosure that is
accessible only to qualified persons.
(2) By suitable permanent, substantial partitions or screens
arranged so that only qualified persons have access to
the space within reach of the live parts. Any openings
in such partitions or screens shall be sized and located
so that persons are not likely to come into accidental
contact with the live parts or to bring conducting objects
into contact with them.
(3) By location on a suitable balcony, gallery, or platform
elevated and arranged so as to exclude unqualified persons.
(4) By elevation of 2.5 m (8 ft) or more above the floor or
other working surface."

There are several references to anything less than 7' above the ground is
considered exposed to physical damage -- 398.15(C) for instance. It is
interesting to note that LFNC is not allowed in an area exposed to physical
damage (NEC 356.12). Therefore a ground-mounted system must be surrounded by
a fence if not 8 feet above the ground.

Even if the wiring is surrounded by a fence, my experience is that
inspectors want to make sure that the wiring does not encourage using the
cable or conduit as a support for someone climbing under the array. I don't
think there is an NEC reference on this, it is just good practice.

Anyone else have something to add?

Bill.




-----Original Message-----
From: Geoff Greenfield [mailto:Geoff at Third-Sun.Com]
Sent: Wednesday, March 17, 2004 6:38 AM
To: RE-wrenches at topica.com
Subject: RE: USE-2, rats and rugrats [RE-wrenches]


I missed the NABCEP question about wearing gloves and
rat-luring-salt-residue was not even one of the answers....

I was more concerned in my post with rugrats -  of the teenaged variety
(possibly suffering from testosterone poisoning).  One reply to my post
mentioned a requirement that anything below 8' have the cables carefully
tucked away so they are not a handhold.  Could someone point me to the NEC
reference I am dealing with here?

Sincerely,

Geoff Greenfield
NABCEP Certified Solar PV Installer TM
GLREA Certified Photovoltaic Systems Integrator/Installer License Number
0211-01

THIRD SUN SOLAR AND WIND POWER Ltd.
340 West State Street, Unit 25
Athens, OH 45701

Phone (740) 597-3111
Fax   (740) 597-1548

www.third-sun.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------











More information about the RE-wrenches mailing list