Goldline controllers on 24 vdc [RE-wrenches]
Allan Sindelar
allan at positiveenergysolar.com
Sun Feb 15 13:30:40 PST 2004
Kirk,
My guru Bristol Stickney's answer:
The SP series can be connected directly to 24 VDC using the low voltage
power supply screw terminials. If you read the spec sheet that comes in the
box with these controllers carefully, you will find a wiring diagram that
shows this.
Best Regards,
Bristol.
As addressed previously, the GL-30 requires a minor modification to connect
it directly to 24VDC. Either a plug kit or two wires soldered to the back of
the circuit board. 24V+ is pin #4 (4th from top) or use the "BR1+" terminal,
labeled on front. 24V- is pin #5 (5th from top), or use the "BR1-" terminal,
also labeled on front.
Allan @+E
----- Original Message -----
From: "Kirk Herander, VSE" <kirk at vtsolar.com>
> To Allan et al:
>
> You said a while ago that the GL-30 controller will operate on 24 vdc. Do
> you have any experience of Goldline's SP series (single stage setpoint)
> being able to do the same.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list