  Bill,

  A 1 1/2 amp, 120 volt draw on an off-grid system is not an acceptable 
solution - at least not for anyone I know; this is the whole reason for the 
discussion. Not including system inefficiencies, this load requires 4.32 kWh 
a day from a PV system - more than a typical refrigerator.

  Also, in spite of the many strong points for Diesel sets, most off-grid 
home owners prefer to have only one fuel delivered to their homes, and since 
propane is already being trucked in, it is the obvious choice. Besides that, 
propane fueled generators are quieter, cleaner and will last as long as 
Diesel sets in residential applications.

  Matt T
  ----- Original Message ----- 
  From: "Bill Haase" <haaseenergy at sbcglobal.net>
  To: <RE-wrenches at topica.com>
  Sent: Wednesday, December 01, 2004 8:58 PM
  Subject: Re: More Kohler RES controller stuff [RE-wrenches]




  ==========================================================
  Extra! Extra! Read all about it! Get the latest weather,
  sports, and lifestyle news you can't afford to miss, all
  at a price you can afford to pay!  Click now!
  http://click.topica.com/caaa9eYbz8QcsbadqCja/TopOffers
  ==========================================================
  Hello to all,



  This is my first time response to "wrenches".  I have been on the list for
  approximately one year, have viewed and read comments and have not 
responded
  in the past.  As a Kohler Generator dealer, an Isuzu/Yanmar/Marathon 
dealer
  and a licensed California Electrical Contractor specializing in off-grid
  systems, I have a couple of comments that might help.



  As far as Kirk Herander's solution, I agree but I don't believe that you
  will ever get Kohler's approval.  I have installed many of the 8.5 and 12
  RES units, either for back up grid power or off-grid.  When used on an
  off-grid system, I have found the easiest solution to maintain the 
generator
  battery is a 1-1/2 Amp small battery charger which sells for approximately
  $28-$32.  This device is totally automatic and will not overcharge.  One
  manufacturer is Schrader which is usually available through Wal Mart. Napa
  Auto Parts also has one similar but without LED lights.  They are 120V AC
  input which can run off of the inverter and draw approximately 18W max on 
a
  low battery.  It has been the easiest solution for the RES battery drain.



  On the subject of finding replacements for the RES, the RMY and the RY gen
  sets, in the last four years I have been using more and more diesel units.
  The three cylinder Isuzu diesel connected to a 8.5KW, 10KW or 12KW 
Marathon
  or Stamford Newage Generator has been an excellent combination.  The
  Marathon Generator is available in either a 4 lead or a 12 lead
  configuration which makes it easy to wire for 120V AC output.  These units
  are available with a 2-wire start and are reasonably priced.  I have also
  use the three cylinder Isuzu connected to a 25KW Generator end which gives
  the ability to have a high current output for 3-4 seconds to start 3-5 HP
  motors, such as large water wells or air conditioning units in off grid
  homes.



  Thank you for this opportunity to share my thoughts.



     -Bill Haase

  Haase Energy Systems, Inc.

  12561 Wilder Rd.

  Red Bluff, CA  96080

  530-527-8989

  530-528-8989 fax.

  haaseenergy at sbcglobal.net


  ----- Original Message ----- 
  From: "Kirk Herander" <kirk at vtsolar.com>
  To: <RE-wrenches at topica.com>
  Sent: Wednesday, December 01, 2004 3:03 PM
  Subject: More Kohler RES controller stuff [RE-wrenches]




  ==========================================================
  Extra! Extra! Read all about it! Get the latest weather,
  sports, and lifestyle news you can't afford to miss, all
  at a price you can afford to pay!  Click now!
  http://click.topica.com/caaa9eYbz8Qcsbew39Ma/TopOffers
  ==========================================================
  Hello Group,

  Supposedly a fix to eliminate the power draw of the RES controller is in 
the
  works at Kohler. I encourage any one who has experienced a dead starting
  battery as a result of controller power drain to complain to your Kohler
  rep. Perhaps that will encourage the factory to hustle on this one. I have
  found out that these controllers were originally designed for some sort of
  marine-based product they make, so it was not engineered for off-grid
  applications (and not really utility backup either). Dumb thing is that 
the
  controller's memory is captive, so no power is required when the generator
  is off.

  BTW, the RES operation manual states that this series is "approved for use
  in backup situations where realible utility power is present". 
Unfortunately
  Kohler is touting the RES as a direct replacement for the RMY series. An
  irate customer pointed this out in the manual to me - so I had to verify
  that the warranty is good in an off-grid situation - which it is.

  Just another pain in the butt that our industry seems to abound in
  sometimes, for which we have to find a work-around. A fix can be easily 
done
  with a DPST 12vdc relay, but I haven't gotten Kohler to approve my wiring
  diagram yet. The remote start (a switch) can energize the relay 
coil(powered
  by the starting battery) and the respective contacts close to both provide
  the remote start signal of the generator, and power to the controller. 
When
  the remote switch opens, it disconnects controller power, thus killing the
  phantom load.

  Kirk

  Vermont Solar Engineering
  Kirk Herander
  North American Board of Certified Energy Practitioners
  Certified Solar PV Installer(TM)
  Xantrex Certified Dealer Charter Member
  NYSERDA-eligible installer
  Vermont Solar and Wind Partner

  PO Box 697
  Burlington, VT. 05402
  www.vermontsolar.com
  www.backeastsolar.com
  800.286.1252 - 802.863.1202
  fax 802.863.7908


  - - - -
  To send a message: RE-wrenches at topica.com

  Archive of previous messages: 
http://lists.topica.com/lists/RE-wrenches/read

  List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

  Check out participant bios: www.mrsharkey.com/wrenches/

  Hosted by Home Power magazine

  Moderator: michael.welch at homepower.com


  - - - -
  To send a message: RE-wrenches at topica.com

  Archive of previous messages: 
http://lists.topica.com/lists/RE-wrenches/read

  List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

  Check out participant bios: www.mrsharkey.com/wrenches/

  Hosted by Home Power magazine

  Moderator: michael.welch at homepower.com

Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Claim your fully stuffed Christmas Stocking now
http://click.topica.com/caacVmdbz8Qcsbz9JC9f/PermissionData
-------------------------------------------------------------------

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read

List rules & etiquette: www.mrsharkey.com/wrenches/etiquette.php

Check out participant bios: www.mrsharkey.com/wrenches/

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: re-wrenches-unsubscribe at topica.com

For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------











</x-flowed>



More information about the RE-wrenches mailing list