on 8/27/04 7:00 PM, Drake at solar at ecoisp.com wrote:
> I soaked a number of cable insulation samples in battery acid. THHN is the
> only type that began to go into solution. See the link below.
>
> http://eagle-access.net/solar/hpart.pdf
THHN is not appropriate for this application. 310-9 Corrosive Conditions
states that "conductors exposed to oils, greases, vapors, gases, fumes,
liquids or other substances having a deleterious effect on the conductor or
insulation shall be of a type suitable for the application."
I contacted American Insulated Wire about what insulation would be
appropriate for use with batteries. Their tech guy emphatically stated that
THHN, a thermoplastic insulation, would be a bad idea. Ideally, the
insulation would be a Hypalon or EPR material, both of which fall under the
term RHW in the listings. Both are a rubber type material with good
characteristics in a corrosive environment.
One caution: Hypalon and EPR are both RHW insulations, but not all RHW
insulations are Hypalon or EPR.
He also advised that using tinned copper conductors was a really good idea.
Phil
Dankoff Solar
Your free subscription is supported by today's sponsor:
-------------------------------------------------------------------
Sponsor a child today through Children International.
Give a desperately poor child hope for a brighter future.
For only $18 a month you can make a difference!
http://click.topica.com/caacvgobz8Qcsbz9JC9f/ChildrenInternational
-------------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list