wire sizing at Higher voltages [RE-wrenches]
Ray Walters
ray at solarray.com
Mon Apr 19 17:14:01 PDT 2004
<x-flowed>
===========================================================
INSTANT CAR INSURANCE QUOTE! Save time, save money, and
get the best deal. Get quote, buy, and print insurance
cards online!
http://click.topica.com/caab599bz8Qcsbz9JC9a/ Insurance4usa.com
===========================================================
Hey Geoff;
No insult taken. I wasn't quit sure, and I thought the group might be tired
of me always questioning our normal ways of doing things. (You guys can
tell me) As far as NEC expertise, Bill Brooks, John Wiles, John Berdner,
and others will give you far better info than I. I'm liable to lead you
astray from the "good book" from time to time.
On the PV wire sizing thread: I found a very interesting thing. While the
2% volt drop is overkill and not cost effective on 12 vdc and even 24vdc
systems, it is pretty close for 48 volt systems at current wire and PV prices.
Now for the big bomb: higher voltage systems (especially over 100 vdc) can
benefit from sizing below 1/2% volt drop! I ran the numbers , and the
watts, while seemingly insignificant as a percentage of the whole system,
are there to be had for $2/ watt or less.
Consider a 50 ft run from array combiner box to inverter at 20 amps. a #10
wire will drop 41 watts at ambient temp. A # 6 wire will only drop 16
watts. So regardless of voltage, you can buy 25 more watts for maybe
another $30 of wire. The #6 would provide 6.7% volt drop for a 12 volt
system, but for a 144 volt system you are only at a 1/2% volt drop. My
point once again is that volt drop isn't as important as power drop. Those
watts are still worth going after; especially in this example they're only
costing $1.20 / watt!
John Berdner or someone with more grid tie experience, can you confirm the
cost benefit of over sizing wire beyond the 2% rule at high voltages? What
is the largest wire the Sunnyboy lugs can accommodate? I know for a 3000
watt array another 25 watts doesn't seem like much, but isn't it still
worth it if the wire cost is less than the PV per watt cost?
Always asking too many questions,
Ray
===========================================================
Bounces like rubber! Shatters like ceramic! Discover Crazy
Aaron's Thinking Putty in grown up handfuls. It's the
creativity unleashing, mood enhancing desk toy!
http://click.topica.com/caab7pJbz8Qcsbz9JC9f/ Crazy Aaron Enterprises
===========================================================
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://lists.topica.com/lists/RE-wrenches/read
List rules & etiquette: www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
For Topica's complete suite of email marketing solutions visit:
http://www.topica.com/?p=TEXFOOTER
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list