Keith,
Although these are very interesting technical discussions, I think you are
faced with a very real code issue. Although the Outback unit may work fine
in conjunction with an SMA inverter, I don't either are listed for that type
of operation (Chris and John will be happy to correct me if I'm wrong). When
the Sunny Island is available in the U.S., that situation will change, but
until then, I think you are stuck. I think the best code-compliant way out
of this mess is the previous suggestion of using the Outback MPPT charge
controller with a slightly higher voltage array (3, 24V modules in series)
and some huge wire.
If the code is not an issue--go nuts--but remember this guy has a lot of
money to pay lawyers.
Bill.
-----Original Message-----
From: Marco [mailto:marco at pvthawaii.com]
Sent: Tuesday, February 10, 2004 11:00 AM
To: RE-wrenches at topica.com
Subject: RE: hybrid grid tie [RE-wrenches]
A number of years ago I purchased a device called a "Solar Maximizer" from a
company in Australia, AES or AEI, I think.
****Buzz*** not listed--sorry--thanks for playing
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list