Self Regulating micro PV system [RE-wrenches]
Bob-O Schultze, Electron Connection
econnect at snowcrest.net
Thu Nov 6 06:36:11 PST 2003
<x-flowed>
Dan and All,
So called self regulating PVs were and are a cruel joke. Less than 36
cells just means the power levels roll off sooner and hardly work at
all in lower light levels. Yet, a 33 cell module still has enough
voltage to overcharge a full battery. That's probably why nobody
makes the culls anymore. I don't believe I've ever seen a 30 cell PV.
Use a CC.
Bob-O
>I saw this in an old Siemens installation instructions, If you wish
>to use a pv module on a wet lead -acid ( I am para-phrasing now),
>they recommended a panel with now more than 30 cells in series -
>lower rated voltage - and to make sure that the maximum charge rate
>for the panel to the ampere-hour rating of the battery bank in
>question was a C/200 rate or less
> In R. Perez's classic "Complete Battery Book", (TAB Books), I
>also believe he says something similar, that's where I 1rst saw a
>rule of thumb guide for self regulating batteries with a PV module.
--
We hang the petty thieves and appoint the great ones to public office. -Aesop
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list