48V relay question [RE-wrenches]
Windy Dankoff, Dankoff Solar
windy at dankoffsolar.com
Tue Oct 21 09:10:57 PDT 2003
<x-flowed>
Allan,
I recommended two single-pole relays on the assumption that you would
want a double-pole relay. The two relays together would produce the
equivalent of one double-pole relay. I do think it's overkill to run
through FOUR series contacts, and also, the more poles, the stronger
the coil has to be, and the more power it uses.
A lot of single-pole relays actually have a 2-series contact
structure, like pressure switches do. You can look in Grainger and
see what I mean.
Windy
At 9:15 PM -0600 10/19/03, Allan Sindelar wrote:
>This idea makes sense--sort of. I can work with two 24V relay coils wired in
>series on 48V. But why do you recommend two 24V single-pole relays, then
>discuss wiring the relay contact circuit in series using two-pole relays? It
>would seem to me that double-pole relays (which are just as readily
>available via Grainger and other sources) would allow a total of FOUR series
>contacts when wired in series for 48V. Am I missing something here? Is it
>just overkill and not needed at 48V?
>
>Thanks,
>Allan at Pos E
>
>----- Original Message -----
>From: "Windy Dankoff, Dankoff Solar" <windy at dankoffsolar.com>
>
>> 1. Install a double-throw relay(s) to act as a transfer switch for
>> the PV circuit. It switches the array to either the pump controller,
>> or to the battery system's array input.
>>
>> 2. Connect the relay coil to battery power through the float switch
>> in the water tank. The float switch can be either NO or NC, just
>> configure the relay contacts accordingly.
>>
>> When the tank fills, relay is actuated, and transfers the PV charge
>> to battery system.
>>
>> 48V relay -- yes, hard to find. Alternative is to get two single-pole
>> 24V relays, and wire their coils in series. This is the exact
>> equivalent (given same contact rating) of a 48V 2-pole relay.
>>
>>
>> About 2-pole transfer relays:
>>
>> Two poles are generally used when you break both + and - (or both hot
>> sides of AC). However, if the system has negative ground (like AC
>> neutral), you are NOT supposed to break the grounded conductor (NEC).
>>
>> Breaking both conductors, people often say, helps to reduce the
>> arcing at the switch contacts, so what do you do? -- OK, it's true,
>> BUT switching through two sets of contacts reduces the arcing no
>> matter WHERE they are located in the circuit. So, wire the relay
>> contact in series, BOTH on the positive line. This helps break the
>> arc when the contacts break. (It distributes the voltage differential
>> between the multiple contacts.)
>>
>> You don't have to go way overboard on relay contact size or quality,
>> because it is unlikely to switch more than about once per day.
>>
>> Windy
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list