hello, here are some of my thoughts. I know it is two
late to change but
I prefer 48 volt strings to keep wire size down.
You mention 880 Amp hr battery, I would like to see
that be a single string of cells. as oposed to a
paralleled strings. For example the potenical
problems with 4 strings of 220 amp hours frightens me.
( Fires as I mentioned before.)
If there are parallel strings I fuse each string with
type T fuses. This is to prevent a problem if one
cell shorts and the other cells back feed into the one
string. They are avaiable in lower ranges.
Another thing I do is use Anderson plugs on the
battery strings. These are the plugs you see on fork
lift trucks. Grainger sells them. This allows a
disconnection means. I like daves idea of putting the
fuse on the bttery but would fear corosion.
I prefer the battery disconnect, the breaker near the
inverter for servicing.
Even if placed in a shed, still use a vented and
sloped cover on the battery box. Unless the shead is
open all the time.
Daryl
--- ASAP POWER! <asap at podnine.com> wrote:
> Wrenches,
> Per Bill's request below, posting this for him...
> Peter at ASAP POWER!
> He monitors the list and so do I, or respond to him
> directly. Thanks to
> all.
>
> Could you post this for me? The RE-wrenches board
> is the only place that
> I figure has a hope of answering this.
>
> ------------------------------
>
> I am installing a remote power system in a
> doublewide trailer at a local
> airport. It will start out as a generator assist
> system, and eventually
> the owner will add solar as his budget allows. It's
> a SW4024 based system
> with 880ah of storage.
>
> The odd part is that he wants the batteries in a
> separate shed; he is
> uncomfortable keeping them indoors (even with a
> battery box) and is
> concerned that the trailer will not support their
> weight. This seems like
> a reasonable concern. As a result, the battery
> cables will have to run
> approximately 10 feet. I'm specifying 4/0 cabling
> and a standard 250A
> Xantrex DC disco near the inverter. The cables will
> be run outdoors via 2"
> EMT so they'll be reasonably well protected. My
> question is - is it
> worthwhile to install an additional 250A fuse in the
> battery shed
> itself? It seems like a bad idea to leave that much
> cable unprotected. Or
> would it make more sense to simply move the DC disco
> to the battery shed?
>
>
> --Bill von Novak
> billvon at dropzone.com
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages:
> http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette:
> http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios:
> www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
__________________________________
Do you Yahoo!?
Yahoo! SiteBuilder - Free, easy-to-use web site design software
http://sitebuilder.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list