Outback HBX mode [RE-wrenches]
Christopher Freitas - OutBack Power
cfreitas at outbackpower.com
Mon Sep 15 15:05:20 PDT 2003
The transistion from Grid to Inverter and Inverter to Grid are both
fully phase synchronized - so very little flicker is noticeable and we
have tested it with loads operating without any issues. It is at least
as good as a SW. With the OutBack inverters we also have coordinated the
operation of the inverter's AC transfer switches from the Master to the
Slaves - so you won't have issues with one leg of the AC system on
inverter while the other AC leg is still on the utility grid...
If your grid voltage typically varies much from 120 VAC then the
switchover either way will be a little more noticeable, as we don't
match the AC voltages before transfering - but you can use or field
calibration adjustment ability to tweek it up or down a few AC volts to
match the relative trend of your utility power. Even if this is not done
the amout of flicker would be similar to a fridge start or other medium
sized AC load with grid power.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
Victor Creazzi wrote:
>
> Christopher,
>
> Thank you for your discription of HBX, it sounds
> exactly how I usually run my SW with a lot of manual
> intervention. I am curious about the actual switching
> between grid and inverter. Is the switching
> syncronized like the SW where the inverter is in phase
> with the grid before transfer occurs, or is it simply
> a relay transfer. If the later what is the effect to
> appliences and is there a noticable flicker?
>
> Make the wind fun!
> Victor Creazzi
> Aerofire Windpower
>
> __________________________________
> Do you Yahoo!?
> Yahoo! SiteBuilder - Free, easy-to-use web site design software
> http://sitebuilder.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list