Wye-Wye to 100kW Xantrex blows utility meter fuse [RE-wrenches]
William Korthof
wkorthof at earthlink.net
Wed Sep 3 11:21:39 PDT 2003
<x-flowed>
We just put in one of the 225 kVA units, and it *is* sensitive
to phase rotation (no automatic rotation matching).
The manual correctly points this out. With backward rotation,
the phase currents are unbalanced and output power is lower.
/wk
>Thanks.. it was 2/0 wire. Sorry
>Imbalanced phases... hmmm possibility. I expect we'd refer that problem to
>Xantrex.
>Phase rotation... not sure how that would play. The inverter should match
>the phase and rotation.
>
>Thanks for the comments!
>
>Mark Robinson
>
>VP Sales and Marketing
>
>Nextek Power Systems, Inc.
>
>89 Cabot Court, Suite L
>
>Hauppauge, NY 11788
>
>(603) 305-1942
>
>www.NextekPower.com
>
>
>-----Original Message-----
>From: Bill Brooks [mailto:billb at endecon.com]
>Sent: Tuesday, September 02, 2003 12:24 PM
>To: RE-wrenches at topica.com
>Subject: RE: Wye-Wye to 100kW Xantrex blows utility meter fuse
>[RE-wrenches]
>
>
>Mark,
>
>Why are you using #2 Wire? Seems too small to me. You could be overheating
>the wire and fuse and the fuse is failing based on temperature, not current.
>Increase your wire size to #1/0 copper or #4/0 aluminum, and your problem
>may resolve itself.
>
>Bill.
>
>-----Original Message-----
>From: Mark Robinson [mailto:Mark at TheEnergyGrid.com]
>Sent: Tuesday, September 02, 2003 8:30 AM
>To: RE-wrenches at topica.com
>Subject: Wye-Wye to 100kW Xantrex blows utility meter fuse [RE-wrenches]
>
>
>Just finished installing a 124kw system in El Cajon. (very sweet.. see
>photos at www.Nextekpower.com) 4kW is connected to the Nextek DC lighting
>system... that part works great. 120k is connected to a 100k PV-100208
>Xantrex. We're blowing the AC fuse on the C leg at the utility meter and we
>think it may have to do with the isolation transformer.
>If you've had any experience with this, please let me know.
>
>Here are the Details:
>SDGE comes in with 480/277 3 phase Wye transformer.
>Ideally, It would make sense to use a Wye Delta Isolation transformer to the
>Xantrex but, because of costs (and with the blessings of Xantrex) we used a
>Wye-Wye with and X0 not connected (floating).
>At the Utility meter, and all-in-1 test section with pullout fuses, the
>three phases are protected with JLLS 150 AMp Fuses. The C Phase keeps
>blowing and the #2 wires are hot.
>No Unusual THD reading although there is 6A on the neutral, which Xantrex
>says is normal (??) in a system this size.
>Xantrex says we should remove the connection to H0 at the transformer and
>replace the fuse with a 175 AMP... suitable for the wire but not ideal
>according to the 125% rule.
>
>Thoughts?
>
>Mark Robinson
>The Energy Grid
>
>
>VP Sales and Marketing
>
>Nextek Power Systems, Inc.
>
>89 Cabot Court, Suite L
>
>Hauppauge, NY 11788
>
>(603) 305-1942
>
>www.NextekPower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
</x-flowed>
More information about the RE-wrenches
mailing list