3648 question/jay peltz [RE-wrenches]
Jay Peltz, Peltz Power
jay at asis.com
Tue Sep 2 20:44:20 PDT 2003
Hi Christopher,
Many thanks for the info.
I've got more FX's going in, keep up the good work,
jay
----- Original Message -----
From: "Christopher Freitas - OutBack Power" <cfreitas at outbackpower.com>
To: <RE-wrenches at topica.com>
Cc: <rgudgel at outbackpower.com>
Sent: Tuesday, September 02, 2003 11:26 AM
Subject: RE: 3648 question/jay peltz [RE-wrenches]
> jay peltz wrote:
> > Say with the 3648 do I use the same 100 amp breaker? or should I go with
> > the next size up?
>
> The 100 amp breakers are somewhat acceptable but are at the limit:
>
> 3600 / 48 / .90 * 1.25 = 104 amps
>
> The real issue is that the VFX can do over 4200 watts for 30 minutes
> from a cold start - so I advise using the 175 amp breaker when possible
> to avoid the possibility of tripping the DC breakers. The larger 1.5"
> wide "GJ" type breakers also have a lot more time delay in my experience
> than the smaller 1" wide breakers.
>
> > Also what is the status of the autogenstart situation?
>
> We are working on it. I am just finishing up the latest additions to
> the "advanced generator start specification" document and am willing to
> forward a copy of it to anyone interested (email me). Any and all
> comments would be appreciated and considered in the development process.
>
> The OutBack "advanced generator start system" only requires that the
> MATE be upgraded - not the inverter - so adding it to any exisiting
> OutBack inverter systems will be easy.
>
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas at outbackpower.com www.outbackpower.com
> Tel 360 435 6030 Arlington WA USA
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list