Grid-Tie Stumper (for me) [RE-wrenches]
Bill Brooks
billb at endecon.com
Mon Apr 14 09:27:18 PDT 2003
Mo,
I'm a little confused. Does your message suggest that they turned off the PV
system or left it on for the test billing period? If the PV system was
turned off, you have a valid baseline and only faults in the wiring from the
PV disconnect to the main service panel could be causing additional power
usage by the PV system. If the PV system was on, then the output of the
SunnyBoy would have to be added to their consumption (and wiring problems up
to the inverter could factor into the additional usage). Does the SunnyBoy
have a meter?
Bill.
-----Original Message-----
From: Mo Rousso [mailto:mrousso at heliopower.com]
Sent: Sunday, April 13, 2003 11:12 PM
To: RE-wrenches at topica.com
Subject: Grid-Tie Stumper (for me) [RE-wrenches]
Wrenches,
I¹ve encountered a situation that puzzles me.
Around 2 months ago, I went on a service call to investigate a system whose
performance was not meeting the homeowner¹s expectations. This system was
installed by another company and I had no knowledge of the installation
prior to my visit.
The system is composed of 1 SMA SWR2500U-SBD and 10 BP Solar SX-150S. The
owner claimed that their utility bill actually increased with the solar
system operating. I read their bills and the latter bills were indeed
higher. I looked at the meter and it appeared to be able to spin backwards
without a problem. Putting my trusty Fluke on the usual inverter terminals
and wires showed appropriate numbers.
I suggested that we needed to collect some data over the next billing period
or two. I suggested that we call Edison and request a physical meter read
since it was conceivable that due to their locked gate and large dog
estimated reads were occurring. I further suggested that once the physical
read was done, that the PV system be turned off and we collect some baseline
data. I was suspicious that their energy habits had changed and that their
consumption had increased. I asked them to be cognizant of their energy
usage patterns and not to make any changes during the course of our trials.
At the start of the next billing cycle, they were to continue using power in
the same manner as the preceding billing period, but with the PV system back
on. Well, that period is now over and the bills are significantly higher
again! They are considering having their PV system removed from their home
not too cool.
Any suggestions on other avenues to explore? Could the PV system
installation have caused some sort of path for those pesky electrons to
disappear down? Are aliens to blame??? :)
Thanks in advance for any guidance I appreciate the collective wisdom
available here. I need to return to the home this coming week.
Mo
--
Mo Rousso
President
HelioPower
Renewable Energy Systems
Remote Power Solutions
mrousso at heliopower.com
www.heliopower.com
760.451.9374
--
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^^===============================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^^===============================================================
More information about the RE-wrenches
mailing list