Need help selecting an inverter [RE-wrenches]
Darryl Thayer
daryl_solar at yahoo.com
Fri Oct 24 08:10:49 PDT 2003
Hello to all
And thanks for the help
When I asked this back in September, I had a 2 stacked
SW5548 inverter system that would not reliable start a
large pump. (kicked out on overload) Many replied that
I needed an Outback three stack or four inverter
stack.
The back ground load was from 2 to 25 amps When the
pump started the pump surge was 130 amps on grid, and
30 amps running. The pump runs less than a minute.
Success! I installed a Outback Quad stack, VFX3648 the
installation looks good and functions perfectly. I
started the pump from several conditions, never failed
once. The amazing thing to me is to see the system
with one inverter running, the 7 hp pump start and the
system immedatly has all four inverters running.
One strange thing, the surge on line power is 130
amps, by my peak hold greenlee clamp on. When I start
from the inverters the peak hold is only 100 amps?
strange because you can not tell the difference in the
pump starting!
Thanks to all
Daryl
__________________________________
Do you Yahoo!?
The New Yahoo! Shopping - with improved product search
http://shopping.yahoo.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list