A mystery to me..... [RE-wrenches]
Roy Dyngen
roy.dyngen at xantrex.com
Mon Oct 20 10:48:15 PDT 2003
Hello Daryl,
I would agree with those that are pointing to the batteries/cables as the
source of your problem. If it were not a battery/cable issue, with a
voltage drop as large as you are experiencing, it would mean an awful lot of
power being dissipated somewhere. If this was not in loads and internal to
the inverter, I believe the smoke would have been let out of the inverter.
Roy Dyngen
Xantrex Technology Inc.
-----Original Message-----
From: penobscotsolar at midmaine.com [mailto:penobscotsolar at midmaine.com]
Sent: Saturday, October 18, 2003 2:19 PM
To: RE-wrenches at topica.com
Subject: A mystery to me..... [RE-wrenches]
Hello all,
I'm having no success in troubleshooting a system we installed almost two
years ago that is three hours travel time each way. It has operated
flawlessly since installation. We have had no lightning in the area for
months.
The system is an SW4048-PP with 24 Surrette KS-25 batteries. It was
originally set up for generator only use (against my recommendations) but
they quickly added a 1.2 KW array within the year. We aded an Outback MX-60
to the system this last July.
I arrived at the site with replacement inverter in hand. We started up
the original inverter with manual bypass breakers both off. It ran fine,
starting up and going into search after 20 seconds or so. Setting it to ON,
again, it ran fine. We turned off the main in the house and threw the
inverter breaker in the bypass and it continued to run fine. We turned off
all the breakers in the main panel and turned the main on and it ran fine.
We threw the first breaker and it continued to run fine. We turned off the
first breaker and continued in this manner until we threw a breaker (
labeled track lighting) and I saw the battery voltage suddenly drop from
54.4 volts to 27.2. The inverter shut down with no error reading and without
any breaker tripping anywhere. We shut off this breaker and turned the
inverter back on. It ran fine.
We continued on and found 2 breakers which powered sub-panels both had
the same effect. One sub powered a Grundfos 1/3 hp SQ-O series 110 VAC
submersible, among other things (mostly lights in the room where the sub
panel is). It seemed as though certain loads were dragging the inverter
down.
To shorten this story, we replaced the inverter and voila! the same
problem!!!!!
When they power the house with the generator through the manual bypass
switch everything runs fine. The system has separate structure ground (for
the array) and system ground (the electrical systems ground)
WHAT AM I MISSING???
Daryl
Penobscot Solar Design
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: roy.dyngen at xantrex.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bd0AMh.cm95LmR5
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list