A mystery to me..... [RE-wrenches]

penobscotsolar at midmaine.com penobscotsolar at midmaine.com
Sun Oct 19 14:04:44 PDT 2003


<x-flowed>
Matt,
  I'm sure you're right. Thanks so much (and thanks Jeff and Clive) and this 
is what makes this list so valuable. Thanks, Michael!
Daryl
Penobscot Solar Design 


Matt Tritt writes: 

> Hi Daryl, 
> 
> Ooooh. 16.7 volts when a heavy load is applied HAS to mean a problem with
> the battery/cables.

> 
> How often do they equalize with the generator? Perhaps they only run on
> solar and never bother with frequent heavy charging? This also sounds like
> things may appear normal under light loads (surface charge readings) but go
> in the toilet when substantial demands are put on the bank. 
> 
> Matt T
> ----- Original Message ----- 
> From: <penobscotsolar at midmaine.com>
> To: <RE-wrenches at topica.com>
> Sent: Sunday, October 19, 2003 1:34 PM
> Subject: Re: A mystery to me..... [RE-wrenches] 
> 
> 
>> Hi Matt,
>>   Thanks, I checked the batteries somewhat but I'll do better when I next
> go
>> up there. One thing I left out is that when the leg with the well pump
> went
>> on and dragged the inverter down the battery bank went down to 16.7 volts
>> from 54.4 v Do you still think it might be the batteries? I hear you when
>> you say more than one crimp could be bad..... Remember, this is a single
>> series string of 2 volt cells.
>> Daryl
>> Penobscot Solar Design 
>>
>> 
>>
>> Matt Tritt writes: 
>>
>> > Daryl,
>> >
>> > I'd bet that the problem is with the batteries, not the inverter.
>> >
>> > I would check for a bad inter-battery connection or a series-string
>> > connection, possibly a bad crimp(s). Dropping to 27.2 volts would
>> > indicate that the problem is at the end of a 4 battery string.
>> >
>> > Matt T
>> >
>> > -----Original Message-----
>> > From: penobscotsolar at midmaine.com [mailto:penobscotsolar at midmaine.com]
>> > Sent: Saturday, October 18, 2003 2:19 PM
>> > To: RE-wrenches at topica.com
>> > Subject: A mystery to me..... [RE-wrenches]
>> >
>> >
>> > Hello all,
>> >    I'm having no success in troubleshooting a system we installed almost
>> > two
>> > years ago that is three hours travel time each way. It has operated
>> > flawlessly since installation. We have had no lightning in the area for
>> > months.
>> >    The system is an SW4048-PP with 24 Surrette KS-25 batteries. It was
>> > originally set up for generator only use (against my recommendations)
>> > but
>> > they quickly added a 1.2 KW array within the year. We aded an Outback
>> > MX-60
>> > to the system this last July.
>> >    I arrived at the site with replacement inverter in hand. We started
>> > up
>> > the original inverter with manual bypass breakers both off. It ran fine,
>> >
>> > starting up and going into search after 20 seconds or so. Setting it to
>> > ON,
>> > again, it ran fine. We turned off the main in the house and threw the
>> > inverter breaker in the bypass and it continued to run fine. We turned
>> > off
>> > all the breakers in the main panel and turned the main on and it ran
>> > fine.
>> > We threw the first breaker and it continued to run fine. We turned off
>> > the
>> > first breaker and continued in this manner until we threw a breaker (
>> > labeled track lighting) and I saw the battery voltage suddenly drop from
>> >
>> > 54.4 volts to 27.2. The inverter shut down with no error reading and
>> > without
>> > any breaker tripping anywhere. We shut off this breaker and turned the
>> > inverter back on. It ran fine.
>> >     We continued on and found 2 breakers which powered sub-panels both
>> > had
>> > the same effect. One sub powered a Grundfos 1/3 hp SQ-O series 110 VAC
>> > submersible, among other things (mostly lights in the room where the sub
>> >
>> > panel is). It seemed as though certain loads were dragging the inverter
>> > down.
>> >     To shorten this story, we replaced the inverter and voila! the same
>> > problem!!!!!
>> >     When they power the house with the generator through the manual
>> > bypass
>> > switch everything runs fine. The system has separate structure ground
>> > (for
>> > the array) and system ground (the electrical systems ground)
>> >      WHAT AM I MISSING???
>> > Daryl
>> > Penobscot Solar Design
>> >
>> > - - - -
>> > To send a message: RE-wrenches at topica.com
>> >
>> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>> >
>> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>> >
>> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
>> >
>> > Hosted by Home Power magazine
>> >
>> > Moderator: michael.welch at homepower.com
>> > --^----------------------------------------------------------------
>> > This email was sent to: solarone at charter.net
>> >
>> > EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.badqCj.c29sYXJv
>> > Or send an email to: RE-wrenches-unsubscribe at topica.com
>> >
>> > TOPICA - Start your own email discussion group. FREE!
>> > http://www.topica.com/partner/tag02/create/index2.html
>> > --^---------------------------------------------------------------- 
>> >
>> > - - - -
>> > To send a message: RE-wrenches at topica.com
>> >
>> > Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>> >
>> > List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>> >
>> > Check out participant bios: www.mrsharkey.com/wrenches/index.html
>> >
>> > Hosted by Home Power magazine
>> >
>> > Moderator: michael.welch at homepower.com
>> > --^----------------------------------------------------------------
>> > This email was sent to: penobscotsolar at midmaine.com
>> >
>> > EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bbfDhm.cGVub2Jz
>> > Or send an email to: RE-wrenches-unsubscribe at topica.com
>> >
>> > TOPICA - Start your own email discussion group. FREE!
>> > http://www.topica.com/partner/tag02/create/index2.html
>> > --^---------------------------------------------------------------- 
>> >
>> >
>> > 
>>
>>
>> - - - -
>> To send a message: RE-wrenches at topica.com 
>>
>> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/ 
>>
>> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm 
>>
>> Check out participant bios: www.mrsharkey.com/wrenches/index.html 
>>
>> Hosted by Home Power magazine 
>>
>> Moderator: michael.welch at homepower.com
>> --^----------------------------------------------------------------
>> This email was sent to: solarone at charter.net 
>>
>> EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.badqCj.c29sYXJv
>> Or send an email to: RE-wrenches-unsubscribe at topica.com 
>>
>> TOPICA - Start your own email discussion group. FREE!
>> http://www.topica.com/partner/tag02/create/index2.html
>> --^---------------------------------------------------------------- 
>>
> 
> - - - -
> To send a message: RE-wrenches at topica.com 
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/ 
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm 
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html 
> 
> Hosted by Home Power magazine 
> 
> Moderator: michael.welch at homepower.com
> --^----------------------------------------------------------------
> This email was sent to: penobscotsolar at midmaine.com 
> 
> EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bbfDhm.cGVub2Jz
> Or send an email to: RE-wrenches-unsubscribe at topica.com 
> 
> TOPICA - Start your own email discussion group. FREE!
> http://www.topica.com/partner/tag02/create/index2.html
> --^---------------------------------------------------------------- 
> 
>  
> 
 

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------


</x-flowed>



More information about the RE-wrenches mailing list