The FX replaced a Trace 2024SB or 2524SB, the series before the U series. He
took a lightning hit, and fast repair service (and in many cases slow repair
service) is gone for this series.
The FX2024 has a 60A charge rate. That's C/20 on either string choice.
What's the problem?
----- Original Message -----
From: "blair Tump may" <tump at midcoast.com>
> Allen what inverter was he replacing?
>
> The FX / Outback inverters are limited w/ their DC charge rate. A large
> cell, we also spec the KS series 2 volt cells, will take for ever to
> charge/ a generator w/ a single inverter.
Blair, I missed your point here:
> The other advantage we always
> stress, in the event a cell goes bad, we can reset the inverter's low
> voltage set points, remove the cell, contact RAE battery and have Roy send
> a replacement cell ASAP. Can't do that w/ those golf carts...... System
> will still work while waiting for a replacment.
Thanks,
Allan
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list