ProSine 2.0 glitches [RE-wrenches]
Christopher Freitas - OutBack Power
cfreitas at outbackpower.com
Fri Sep 26 16:25:34 PDT 2003
I pulled out my notebook from the day you were here when we discussed
your test results and here is what I had recorded:
The VFX 3524 charged at 85 amps DC but the AC voltage was sagging
The SW+ 2524 was putting out 60 amps DC from your generator
So the increased charger output was be 85A/60A = 1.41 or 41% more.
I made a mistake in my earlier post and did it the other way 60/85 =
0.70 which I then incorrectly converted to being a 30% increase - need
to not type and do math at the same time...
When both operate at their rated specs the increase would then be:
VFX 3524 85 amps 85A/70A = 1.21% or a 21% increase for the VFX
SW+ 2524 70 amps
The ProSine is a 12 vdc only unit and has a charger rated at 100 amps DC
- which would be the same as a 50 amps DC charger on a 24 vdc system -
but it is only a 2kW unit so not really a fair comparison.
ezra at lasqueti.net wrote:
> To be totally nit-picky it was delivering about 21% more current to
> batteries than either of the other inverters mentioned.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list