Eric,
The official recommendation from Grundfos is #12 wire even at 3000 ft
length. Or use the pressure switch setup. Let us know what you use and
how it works out. Thanks
Brad
Brad Bassett wrote:
>
> Eric,
>
> Yes you can increase the distance to the float switch by increasing the
> wire size. The 330ft limit is assuming the same wire size as the float
> switch is made with. If it is assumed that the float switch uses # 18
> wire, then to get the same voltage drop over 3000 ft you would have to
> use # 8 wire. It may be that smaller wire would work, but am not sure. I
>
> will try to get further info from Grundfos.
>
> Brad
>
>
> erics wrote:
> >
> > I have a customer that wants to use a Grundfos 6 SQF-2 to pump from one
> > storage tank about 3000' and up 250' to another storage tank.
> > My question is about the distance and a float switch conductor.
> > Grundfos' CU200 float controller can only have a max. of 330' between
> > float to controller. Anyone done this for 3000'? Can I increase wire
> > size?
>
> >
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list