HU361 as Combiner/Disconnect [RE-wrenches]
Jeff Clearwater
clrwater at earthlink.net
Tue Jun 3 11:45:10 PDT 2003
<x-flowed>
Hi Matt,
Yes I see your points. I was trying to get away with only one line
to the SB by combining a the HU361 but if each lug is rated for only
one cu landing that won't work and it defeats what I was after.
But it strikes me as very odd that a PSSB breaker can be rated to two
conductors/lug but not the nice big lugs on a HU361. Any chance of
that rating changing? John B?
Thanks,
Jeff C.
>
>1. The Line (Array) is required to be landed on the top lugs of the
>Disco. (Behind the arc-shield)
My drawing was electrical not orientation - but yes thanks for the
reminder of using the shieded side correctly.
>
>2. The lugs are rated for single-conductor landing only.
>
>My recommendation, at least relating to the Disco at the Inverter, is to
>run the two "switched hots" (from the bottom lugs) to the SB. The SB
>has 3 DC Input terminals for a reason. This is it.
>
>Regarding the use of an HU361 at dual locations, I think you will find
>you can easily run the extra pair between disconnects in the same
>conduit you are already installing.
>
>Try it this way:
>
>ARRAY
>
>+ from String 1
> + from String 2
>l l
>0 0 0
>
> ROOF Disco
>
>0 0 0
>l l
>l l
>l l
>+ + to 2nd Disco; Line 3
>to 2nd Disco; Line 1
>l l
>l l ________ IN CONDUIT
>l l
>
>
>+ from Roof Disco; Load 1
> + from Roof Disco; Load 3
>l l
>0 0 0
>
> INVERTER DISCO
>
>0 0 0
>l l
>l l
>l l
>+ + to SB DC Input
>to SB DC Input
>
>
>Hope this helps...
>
>Pray for Sun and No Tanlines!
>
>Matt Lafferty
>Universal Energies Institute
>mlafferty at universalenergies.com
>(916) 422-9772
>(916) 628-7694 Cell
>(916) 914-2247 Fax
>www.universalenergies.com
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
--
~~~~~~~~~~~~~
Jeff Clearwater
Village Power Design Associates
Sustainable Energy & Water Solutions for Home & Village
877-SOLARVillage
PO Box 115
Boonville, CA 95415
61 Baker Rd
Shutesbury, MA 01072
413-256-6777, 413-825-0372 (Fax)
~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~`~
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list