Grid-Tied SW output meter [RE-wrenches]

Christopher Freitas - OutBack Power cfreitas at outbackpower.com
Wed Mar 19 10:53:30 PST 2003


Yes - this method does work for single SW installations.  For dual I 
think you would have to use two separate meters.  I would first verify 
that it does work before the installation to make sure the hookup is 
correct - you don't want to come back a month later and find some odd 
results...

The idea of this technique is that the pass-thru AC current (power going 
directly from the grid to the loads will not be recorded as the AC 
current going out cancels the AC current coming in.  Only the AC current 
going either out to the loads or out to the grid is added to the meter - 
both as positive.  Any current coming in from the grid that is used to 
battery charge will also be subtracted from the meter reading - and then 
would be added back in correctly as a positive value if it was sold 
again later on (with the losses taken in account).  

I have done this trick with data acquistion systems and single Current 
Transformers (CTs) - just not with a single AC kilowatt meter however. I 
have used multiple meters to record input and output current and it gets 
really confusing quick when you looking at them on the wall.  

Christopher
 

  





Todd Cory, Mt. Shasta Energy Services wrote:
> Did any one want to comment on whether this might work? It sounds 
> interesting
> to me.
> 
> Todd
> 
> 
> William Korthof wrote:
> 
> > I had an idea for this situation... for an installation with one
> > SW inverter (120 Vac only) perhaps a single meter could
> > be used to measure both outputs from the inverter---use
> > the "line 1" side of the meter for the grid side of the meter
> > and "line 2" for the load side. I think it would need to be a
> > mechanical type meter with a neutral coil connection
> > (ie, "single phase" meter for use on 120/208 3-phase).
> > The neutral connection should allow the two lines to be
> > measured properly and independently, whether they are
> > in phase (normal operation), or otherwise (grid off, grid
> > frequency error...).
> >
> > /wk
> >
> > At 10:57 AM 3/12/03 -0800, you wrote:
> > >The new CEC guidelines require a "System Performance Meter" for grid 
> > >tied
> > >systems which receive their final after March 31, 2003. We occasionally
> > >use an SW with back-up batteries to serve a critical load sub-panel. I
> > >think this is how we can meter both the output going to the critical 
> > >loads
> > >as well as the main panel/grid during daytime energy production and
> > >account for power the inverter will feed through from the grid at night.
> > >One kWh meter on the grid AC IN 1 side of the inverter and another on 
> > >the
> > >AC Out to the critical loads. Total output equals the total of both of
> > >them. The grid power used for the AC Out loads will be subtracted from 
> > >the
> > >AC In meter which cancels the amount added to the AC Out meter.
> > >
> > >Does this make sense and/or is there an easier way to do this?
> > >
> > >Thanks,
> > >--
> > >David Henry
> > >Harmony Farm Supply
> > >3244 Hwy 116 N., Sebastopol, CA 95472
> > >707-823-9125 X14 voice
> > >707-823-1734 fax
> > >david at harmonyfarm.com
> > >www.harmonyfarm.com
> 
> 
> 



Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com  www.outbackpower.com
Tel 360 435 6030  Arlington WA USA

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael_welch at sbcglobal.net

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================




More information about the RE-wrenches mailing list