John Wiles & 600 VDC switches [RE-wrenches]
Jay Peltz, Peltz Power
jay at asis.com
Tue Feb 11 19:22:39 PST 2003
Hi Bill,
The Cutler Hammer unit I installed specially stated that the use of a jumper
between terminals 1 and 3 made it 600VDC. Yes that makes it only 1 pole,
but this information was IN THE INSTUCTIONS that came with the unit.
So I'm curious why would you state that this is not legal.. Mind you its
been inspected by PG&E, the County and the State, not that that matters and
yes they are not the experts.
I should point out that this system was a single string of 10 panels.
You also made some mention of a possible problem with paralleling stings of
panels for the SB. Now is this if they are connected in the lug on the
disconnect or just generically that you cannot?
Thanks,
jay