SB's in high temperature (was lemmings) [RE-wrenches]
jberdner at sma-america.com
jberdner at sma-america.com
Thu Feb 6 16:11:30 PST 2003
Joel:
UL established the power rating our inverter at 2500 Watts.
You can certainly design the system around 2200 Watts and it will run
just fine.
I am a member of the Standards committee at UL and we are proposing
changing to UL 1741 the way power ratings are established to make power
rating better reflect real world conditions. This will give us a level
playing field for inverter power ratings (for both grid tied and off
grid) that better reflects the needs of customers.
If you have any questions, or if I can be of any further assistance,
please do not hesitate to contact me.
Best Regards,
John Berdner
SMA America, Inc.
12438 Loma Rica Drive, Unit C
Grass Valley, CA 95945
530.273.4595 (voice)
530.274.7271 (fax)
-----Original Message-----
From: Joel Davidson [mailto:joeldavidson at earthlink.net]
Sent: Thursday, February 06, 2003 3:05 PM
To: RE-wrenches at topica.com
Subject: Re: SB's in high temperature (was lemmings) [RE-wrenches]
John,
I think you will sell just as many Sunny Boy inverters if you rate them
2.2
kW instead of 2.5 kW.
Best regards,
Joel Davidson
jberdner at sma-america.com wrote:
> Graham:
>
> While you can use the Sunny Boy + Breeze scenario there is another
more
> conservative approach is reliability and longevity are of paramount
> concern.
> If you undersize the array by 10 to 15% there should be no issue at
103
> F. This approach adds no additional hardware and not pushing the
> inverter to its limits will certainly extend it's life. There is a
rule
> of thumb in power electronics (I forget who's rule it is) - for every
> 10C decrease in temperature the life is doubled. This is true for all
> power electronics not just our inverters.
>
> Fan Life - In building the Sunny Breeze we selected a fan with 30 k
> hours MTBF. The 2 to 3 year estimate for life is out estimate for
> outdoor, unprotected mounting. If mounted indoors it will run more
> frequently but the life of the fan should certainly be well beyond the
> warranty period.
>
> If you have any questions, or if I can be of any further assistance,
> please do not hesitate to contact me.
>
> Best Regards,
>
> John Berdner
>
> SMA America, Inc.
> 12438 Loma Rica Drive, Unit C
> Grass Valley, CA 95945
> 530.273.4595 (voice)
> 530.274.7271 (fax)
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list