MC connectors, warranties and PV system life [RE-wrenches]
Robert Warren
robertwarren at mail.com
Sat Feb 1 16:14:48 PST 2003
Joel,
Over here in Europe, Multi-Contact connectors are quite standard, for
two major reason: they are double insulated and also provide touch-safe
installation safety. Pretty much 99.99% of the systems over here are
grid connected, using higher voltages up to 500 VDC feeding into first a
DC disconnect , then from this into the inverter, again with MC
connectors. We commonly use electrical tray/channels which are open,
rather than conduit, and use zip-ties to the tray slots.
As for arcing, the MC connectors are not rated for disconnecting under
live conditions, which is why we always use a DC disconnect. The
disconnect box can also be used for paralleling strings & lightning
protection. We make our own, with substantial blocking diodes, heat sink
mounted. Multi Contact has a new variety of cable available, as you can
see on their web site. The Japanese manufacturers now make a very
similar product, but Kaneka, on this 100 kilowatt job I did recently for
a sports stadium in Birmingham, came with the MC cables factory
installed. You can see the details of this installation at
http://www.solarcentury.co.uk/content.jsp?sectno=1&subno=5
then click on Alexander Stadium.
Robert Warren
Senior Engineer
Solar Century
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael_welch at sbcglobal.net
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
==^================================================================
More information about the RE-wrenches
mailing list