contactor cuestions [RE-wrenches]
Marco
marco at pvthawaii.com
Fri Dec 5 12:05:24 PST 2003
Commercial grid-connected systems using the Xantrex PV series 3-phase
inverters with their dedicated isolation transformers mean that there's
going to be a not insignificant parasitic power loss during the nighttime
hours. According to my own measurements and conversations with others, this
loss can somewhere between 3-5 percent, or even more, of the previous day's
kWh production. One way around these inverter and transformer core losses
would be to install a three-pole contactor/relay that would disconnect the
PV equipment in the evening and reconnect it early the following morning.
The issues as I see them are: 1) extra cost for the labor, contactor and
additional control electronics, and 2) additional means of system failure in
case the contactor stays open. One could use a photosensor to control the
contactor or even a standard mechanical or digital timer.
Has anyone out there gone this route of using a contactor? Any feedback on
the pros and cons?
thanks,
marco
Marco Mangelsdorf
President
ProVision Technologies, Inc.
69 Railroad Avenue, Suite A-7
Hilo, Hawaii 96720 USA
(808) 969-3281, fax 934-7462
www.provisiontechnologies.com
[Non-text portions of this message have been removed]
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
--^----------------------------------------------------------------
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-Wrenches-unsubscribe at topica.com
TOPICA - Start your own email discussion group. FREE!
http://www.topica.com/partner/tag02/create/index2.html
--^----------------------------------------------------------------
More information about the RE-wrenches
mailing list