Ground faults / NEC changes for 2005 [RE-wrenches]
William Miller
wrmiller at slonet.org
Fri Nov 15 22:38:22 PST 2002
Steve:
It is a fallacy to believe that positive voltages are the only source for
current, fault or otherwise. In this case, when the positive at the PV
array was grounded, the negative PV lead was forced to become 48 volts
lower than the battery negative. (When the PV negative was connected, to
the negative buss, it was at 0 volts, but it was pumping the entire SC
current through it. When it was disconnected, it went to - 48).
The negative can not be disconnected by a breaker as there is no breaker
installed in that lead, so we have current in a device that was "shut off."
This was the negative voltage trying to get to the ground rod, back into
the building and back to the shorted positive PV lead. The negative was
one leg of the circuit, the ground and structure the other. Get it?
William
At 10:40 AM 11/15/02 -0800, you wrote:
>
>You stated that all those breakers were manually off and still arcing was
>possible on the board when a screwdriver was applied to it. this suggests
>an additional source of + battery or +PV was available to the board. Were
>there a temp sensor or the external battery current shunt connected to the
>board that could have come in contact with + battery voltage? Any other
>wires? (I would expect a larger wire, and not the temp sensor, would be
>required to bringing that much current)
>Steve Willey steve at backwoodssolar.com
__________________________________________________________________
William Miller
Miller Power and Communications
PO Box 50, Santa Margarita, CA 93453
Voice :805-438-5600 Fax: 805-438-4607 VMail: 805-546-4875
email: wrmiller at slonet.org
http://millerpowerandcomm.com
License No. C-10-773985
_____________________________________________________________
Compatibility:
Word processor: WP7
Spreadsheet: Quatro Pro 7
CAD: Microstation 95, DXF, Visio 4.1T
_____________________________________________________________
"Every decent man is ashamed of the government he lives under."
H. L. Mencken
__________________________________________________________________
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list