High Voltage Charge Controller [RE-wrenches]
Jeffrey Wolfe, Global Resources
global at sover.net
Mon Aug 26 20:02:02 PDT 2002
Travis,
Solar Converters offers several different voltage conversion MPPT units. I
know, as we've fried 10 of them. I know longer have any in the field, the
longest surviving giving up after about 18 months. (Most lasted btwn 18 minutes
and 18 hours on one job. It was a long job, which finally was converted to
48VDC and C40's. Fortunately I'd oversized the wire enough to be ok.)
I'm working with a "prototype" 600VDC system, battery based with an integrated
600VDC charge controller. Made for a "large" system (10kW array, 30 kW inverter)
System could be grid tied, but cannot sell back. Contact me off-list if you
want more info on status of this project.
Otherwise, you've about listed the choices. I know there are folks on-list with
tall pole experience (Kirk Herander at VT Solar Engineering just put a small
array on a 30' stick for a state well project.)
For a 700' run, you're really going to want to run the system at a much higher
voltage, not just 100V. SMA's "Sunny Island" system is supposed to allow Sunny
Boys to feed into it at 240VAC, but that's not ready for UL yet, last I heard.
Might check with John B about it.
Good luck!
Jeff
Quoting "Travis Creswell, Ozark Solar" <ozsolar at ipa.net>:
> I am designing a job where the array is at least 700' from the house
> which
> is in heavy woods and the customer doesn't want to cut any trees down.
> Putting the inverters and batteries nearby to the array doesn't really
> solve
> anything either since the system will be grid tied. That means I would
> need
> to have an AC run from the house to the inverter location then back to
> the
> house again. That's 1400' roundtrip.
>
> What I would really like is a MPPT charge controller that would let me
> run
> the array above 100 volts with 48 volts nominal output for the battery
> bank.
> I have heard of several custom made units but have never seen any.
> Where
> can I get such a thing?
>
> Or maybe I need put the array on top of a 40' pole? Anybody done
> anything
> like that?
>
> Thanks
> Travis Creswell
> Ozark Energy Services
>
> - - - -
> To send a message: RE-wrenches at topica.com
>
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
> Hosted by Home Power magazine
>
> Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list