Are you all putting in these different oriented sub-arrays and parallel strings
with string blocking diodes?
Bill Brooks wrote:
> William,
>
> Once the operating voltage is set by the dominant portion of the array, the
> parallel strings still have a max power voltage that is nearly identical to
> the array in full sun. It may seem counter-intuitive, but temperature
> changes voltage, not irradiance (accept at very low irradiance).
>
> The critical issue is that all the modules in a series string are in the
> same orientation since the operating current needs to match exactly.
> Parallel strings can be in different orientations with little negative
> affect on performance since the operating voltage of each string is nearly
> identical.
>
> Bill.
- - - -