AC/DC in Same Conduit? [RE-wrenches]
Matt Lafferty
pvpro at attbi.com
Thu Jul 11 18:24:46 PDT 2002
Wrenches:
A glimmer of sunshine in Brother Bill's helpful recital! I have been
wandering in the wilderness for forty years! Well, almost forty...
Thanks for digging this out Bill!
Humble Sun Worshipper
-Matt Lafferty
pvpro at attbi.com
Matt Lafferty wrote:
> Mixing of "separately derived" power sources within a single raceway,
> without a physical separation, to my knowledge has always been prohibited.
Brother Bill wrote:
> The chapter and verse of the requirement is in Article 690.4(b)of the holy
> NEC:
>
> (B) Conductors of Different Systems.
> Photovoltaic source circuits and photovoltaic output circuits shall not be
> contained in the same raceway, cable tray, cable, outlet box,
> junction box, or similar fitting as feeders or branch circuits
> of other systems, unless the conductors of the different systems
> are separated by a partition or are connected together.
>
> Here endeth the first lesson.
>
> This doth not refer to DC and AC systems in general. Article 300.3(c)(1)
> doth say:
>
> (1) 600 Volts, Nominal, or Less.
>
> Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and
> dc circuits shall be permitted to occupy the same equipment wiring
> enclosure, cable, or raceway. All conductors shall have an
> insulation rating equal to at least the maximum circuit voltage
> applied to any conductor within the enclosure, cable, or
> raceway.
>
> Exception: For solar photovoltaic systems in accordance with 690.4(B).
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list