I too would like the code reference, Bill. We have been operating on the
principles that:
1) Conductors of different voltages may share the same conduit (raceway,
gutter, etc.) as long as all of the conductors were rated above the voltage
carried by any of the conductors: 600V THHN, TC, etc.
2) Conductors of different voltages (or, in everyday usage, AC and DC) could
not terminate within the same enclosure; that is, conductors of one voltage
could only pass through the enclosure or j-box which terminated or spliced
conductors of another voltage/source.
3) PV source and load circuits could not share the same anything.
Please site specifics, or should we ask Mr. Wiles?
Thanks, Allan at Positive NRG
----- Original Message -----
From: "Todd Cory, Mt. Shasta Energy Services" <toddcory at jps.net>
> Bill can you quote the code where this is specified. I would like to see
> specifically what it says about mixing voltages in one conduit.
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list