William,
>Also, it sounds like you are assuming the shut-downs are caused by grid
>problems. Do you have evidence of that? (After watching the original ST
>inverters shut down hundreds of times, I am convinced it was because the
>MPPT algorithm was too aggressive and, after loading the panels too much,
>the voltage collapsed. You could see the PV volts cave just before the
>shutdown.)
I'm pretty sure it's some of both, but I was told by someone in
Xantrex (I forget who) that a MPPT crash won't trigger a 5 minute
disconnect in the XR, which shouldn't show up as a "V" error fault.
This particular installation is way out in farming country. I'm
betting that every time a big irrigation pump kicks on in the
neighborhood, the grid sags. I've seen it before.
>
>I did a back-to-back comparison between the original ST2500 and the SB2500
>and found the ST to be about 10% less efficient than the SB. Sounds like
>we may be in the same ballpark. This comparison was relevant for the
>periods of time that the ST was running. Frequent shut-downs and the
>subsequent time-outs could reduce the efficiency significantly.
>
>This was actually a trick question as I installed two XRs yesterday, but
>wanted to reserve judgement until I heard from others. One of my two
>inverters had a missing lower line on the display. This was also
>disappointing as I have many of display failures in the original STs.
I had that missing line thing in one of mine too. No doubt the lowest
bidder got the contract....
>
>I'm looking for a reason to use STs rather than Sunny Boys and I haven't
>found one yet. With the SB1800s now shipping (they are shipping, aren't
>they?) the 1500 no longer fills any kind of gap in the product line.
Actually, they aren't shipping just yet. I'm looking to have stock in
mid-July at best.
I'm probably one of the last to find this out, but in case you didn't
know, the SB1800 is a 120vac machine. It needs about 140VDC in and
quits at 400Voc. Might make a bit of a difference in your designs.
I think there is still a place for the STXR 1000. The GC-1000 doesn't
seem to be any more or less impressive.
Best, bob-O
--
Bob-O Schultze, Electron Connection
PO Box 203, Hornbrook, CA 96044
800.945.7587 or 530.475.3402
fax 530-475-3401
www.electronconnection.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
</x-flowed>
More information about the RE-wrenches
mailing list