Inverter Generators? [RE-wrenches]

Travis Creswell, Ozark Solar ozsolar at ipa.net
Wed May 22 08:58:36 PDT 2002


Hi Kurt,

I tested the inverter on my SW4048 yesterday.  It had no problem locking on
to start charging even when the generator was idling. It charged at 30 amps
AC for about 15 minutes until I turned it down to 10 amps AC.  Tri-Metric
showed over 50 amps @ 53 volts on the DC side.  The generator is only rated
at 2800 watts so I felt that was test enough.  I did a crude efficiency test
using a Brand meter for the AC and a Tri-Metric for the DC side. With the AC
charge rate set to 5 amps, the inverter was using around 580 watts and the
Tri-Metric showed 10 amps @ 51 volts (510 watts), approx 88% efficient.  An
interesting note was the Brand Meter showed the inverter's power factor at
.95 at that charge rate and the Power Factor got worse as I turned the
charge rate up.  The DC charge rate seemed very comparable to what I get off
the grid.

Throughout all the changing of charge rates the generator never went out
side the SW's factory set parameters and remained lock on charging the whole
time.  I'm pretty sold on these inverter generators.

Travis
----------
>From: sunwise at cheqnet.net
>To: RE-wrenches at topica.com
>Subject: Re: Inverter Generators? [RE-wrenches]
>Date: Tue, May 21, 2002, 1:06 PM
>

>Travis Creswell, Ozark Solar wrote:
>> 
>> So I bought one for my self.  A Yamaha 120 v, 2800 watt unit that weighs 58
>> lbs.   I power my shop with a SW and will soon test the SW's charger with it.
>> 
>Hey Travis,
>
>I'm interested in hearing how this goes -- Keep us posted -- Kurt
>
>- - - -

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list