Hi Todd,


At 02:21 PM 5/21/02 -0700, you wrote:
>While series fuses in the panel junction boxes sounds like a good idea, it 
>will
>not protect the conductor between the battery/parallel string connection 
>and the
>panel. I thought that was the whole point of series fusing, to protect the 
>wire
>feeding from the PV's.


The series fuses are to protect the modules from reverse current.   When a 
module has a reverse current flow it gives off heat.

Drake




>Todd
>
>
>Drake Chamberlin wrote:
>
> > With Siemens SP 75 modules, with their excellent junction boxes and 15 amp
> > series fuse rating, I think we can safely use a 15 amp series fuse on each
> > string, in the j box, without concern.
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================


</x-flowed>



More information about the RE-wrenches mailing list