The rule is not specific about fuses or not in regards to the Air Cond.
disco, it simply says it is not allowed. I've found over and again that PG&E
does not have issue with fuses anymore. This seemed to have changed about
the same time that we were allowed to use a branch disco rather than the
early days of whole service disco. Obviously, a whole service fused disco
could pose a real nuisance. On my last 3 projects PG&E did not even put the
locks on it saying that the linemen will lock it out when needed only for
service. This sure makes a lot more sense to me. My most recent project has
an existing whole service manual generator transfer switch that can be
locked in any of the 3 positions. PG&E accepted the trans. sw. as a lock-out
(it certainly was not on the "Blessed" list) and acknowledged that if they
were to put a lock on it the customer could not transfer their gen. We all
walked away happy as I was told to "throw the switch".

I wish all of the wrenches could have similar sanity to deal with!

-jeff

> 	From the Solar, Wind & Hydro Powered office of:
> 	Jeff Oldham
> 	Gaiam- Real Goods & Jade Mountain
> 	Design & Consulting Group
> 	11755 Mid. Mtn. Rd.
> 	Potter Valley, CA 95469  USA
> 
> 	Ph: 303.222.3814
> 	Fax: 707.743.1820
> 
> 	www.solardevelopment.com
> 
> 	"When you turn to face the Sun all shadows fall behind you"
> 	- Old African Proverb
> 


-----Original Message-----
From: Michael Welch, Home Power [mailto:michael.welch at homepower.com]
Sent: Wednesday, May 08, 2002 4:33 PM
To: RE-wrenches at topica.com
Subject: RE: Switches [RE-wrenches]


jeff.oldham at realgoods.com wrote at 05:11 PM 05/08/2002 -0600:
  
>BTW- Rule 21 also specifically rejects Air Cond. pull-out type disco's. Too
bad, I like the idea of a $10 disco that no one will ever use.

Isn't the problem with those that they have fuses in them, and the utility
wants no user-serviceable parts in the lockable disconnect? At least that's
the way PG&E described it to us when they nixed ours awhile back.

If the utility's lock is on the unit, and the fuse blows, the utility has to
come out to help change it.
  
Michael Welch
  
------------------------
"The true, unacknowledged purpose of capital punishment is to inspire fear
and awe - fear and awe of the State."
			Edward Abbey
        
Michael Welch, michael.welch at homepower.com www.homepower.com
     Managing Editor, Home Power magazine
     Office Coordinator, Redwood Alliance
     (Not HP mag numbers) 707-822-7884 fax: 707-822-3481

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list