DC Load Center's [RE-wrenches]
Travis Creswell, Ozark Solar
ozsolar at ipa.net
Wed May 1 10:46:07 PDT 2002
They are rating them at 14k AIC at 125 vdc. I was planning on using current
limiting fuses on each string. Inspection is not an issue.
Can your product handle all I need it to plus leave room for expansion?
Travis
OES
----------
>From: Christopher Freitas - OutBack Power <cfreitas at outbackpower.com>
>To: RE-wrenches at topica.com
>Subject: RE: DC Load Center's [RE-wrenches]
>Date: Wed, May 1, 2002, 12:23 PM
>
>> Has anyone every used the Cutler-Hammer Products rated for 125/250
>> VDC? Specifically PRL3a with GHB breakers. Supposedly, it will
>> allow for a main breaker of up to 800 amps and branch circuit
>> breakers of up to 400 amps. All rated at 125/250 VDC. By the way, >
>> just what do they mean by that? According to my local Cutler Hammer >
>> Supplier they supply CH products to a local company who makes and
>> installs Telecomm power houses and they are using them in DC
>> applications.
>
>Be careful with DC ratings on AC breakers - They may be approved for
>very specific applications and installation methods. For example, the
>interruption capacity (called AIC) may not be enough for use with
>batteries or may require "back-up" fusing to be used safely with
>batteries. In Telecom applications it is very common for a current
>limiting fuse to be installed on each string of batteries before leaving
>the battery enclosure ahead of any breakers to limit the fault current.
>This may or may not be allowed on NEC inspected systems.
>
>I wrote an article on DC breakers vs. fuses in 1992 in Home Power which
>is dated but still is useful - here is the link:
>
>www.humboldt1.com/~michael.welch/hp27-26.pdf
>
>The article includes some real hands on testing of DC rated breakers in
>which we blew them apart and caused excessive arcing and damage.
>
>Christopher Freitas
>OutBack Power Systems, Inc.
>cfreitas at outbackpower.com www.outbackpower.com
>Tel 360 435 6030 Arlington WA USA
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list