Trace Charge Controller Ratings [RE-wrenches]
Ray Walters
remotech at taosnm.com
Sun Apr 28 17:47:14 PDT 2002
I use class T pullout disconnects from Boltswitch. UL listed, we make our
own enclosures. I know all of you UL freaks are cringing, but I cringe at
breaker only systems or the overpriced breaker + fuse option.
Why did everyone quit using the Boltswitch disconnect anyway?
Ray
> "I am still wondering how Trace gets away with using only the
> Heinemann breakers as primary protection. While the breakers are rated at
> 25,000 AIC for DC circuits, who wants their equipment to handle that
> current for the delay time required to trip this breaker"
>
>I agree. we always install a class T fuse right next to the positive
>terminal of the battery bank with about 8" long #4/0 cable. Then we run to
>the Heinermann breakers in the Trace panel. This also gives the added
>protection in case the battery box and inverter are located in different
>rooms separated by a wall, with much higher potential for cutting or a short
>between the battery box and the inverter dis-connect that could start a
>fire.
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list