Christopher,

Your comments suggest that nothing will prevent some problems from occurring, if GFIs and fusing aren't able to provide protection. In over 20 years of installing battery-based power systems, I've never installed a GF protection device at the PV or battery primary wiring, seen one installed by anyone else, or seen any damage as a result of not installing one. Not to say it isn't possible (as evidenced by William Millers problem system) but for this occurrence to trigger mass installations of ground fault protectors, which are problematic in themselves, seems a little on the reactionary side, nes pas?

If this issue is so all-fired important, why not include ground fault protection in and for ALL DC control and conversion devices as standard, from the factory? Hmmmmm?--- 
From: "Christopher Freitas - OutBack Power" <cfreitas at outbackpower.com>
To: <RE-wrenches at topica.com>
Sent: Friday, November 15, 2002 5:11 PM
Subject: RE: Ground fault [RE-wrenches]


> > The ground fault is likely the result of the board insulation
> > disappearing.
> 
> Ground fault protection may not have prevented the Solar Boost failure 
> but it can be very helpful in preventing the spread of the damage beyond 
> the original problem.  I have seen wires fall out of loose melted 
> terminal blocks on numerous occasions with many "UL" listed products - 
> causing other problems to occur (such as battery short circuits).  
> 
> Eliminating the ground fault protection and replacing it with fuses or 
> breakers in both the negative and positive conductors will not eliminate 
> the pssibility of risk or damage.  Often a fault can be limited by the 
> material completing the fault circuit - so a fuse or breaker may not 
> trip (especially with a current limited energy source such as PV). There 
> are trade-offs involved with each method of protection.  
> 
> Christopher Freitas
> OutBack Power Systems, Inc.
> cfreitas at outbackpower.com  www.outbackpower.com
> Tel 360 435 6030  Arlington WA USA
> 
> - - - -
> To send a message: RE-wrenches at topica.com
> 
> Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
> 
> List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
> 
> Check out participant bios: www.mrsharkey.com/wrenches/index.html
> 
> Hosted by Home Power magazine
> 
> Moderator: michael.welch at homepower.com
> 
> > 
>
[Non-text portions of this message have been removed]

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^^===============================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^^===============================================================





More information about the RE-wrenches mailing list