> The ground fault is likely the result of the board insulation
> disappearing.
Ground fault protection may not have prevented the Solar Boost failure
but it can be very helpful in preventing the spread of the damage beyond
the original problem. I have seen wires fall out of loose melted
terminal blocks on numerous occasions with many "UL" listed products -
causing other problems to occur (such as battery short circuits).
Eliminating the ground fault protection and replacing it with fuses or
breakers in both the negative and positive conductors will not eliminate
the pssibility of risk or damage. Often a fault can be limited by the
material completing the fault circuit - so a fuse or breaker may not
trip (especially with a current limited energy source such as PV). There
are trade-offs involved with each method of protection.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9.bWljaGFl
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list