Massuh Bill and others,

Here's a teaser.  Let's look at two identically sized PV arrays.  One facing due south at latitude.  The other one is split 50-50 due east and due west at a slope of, say, 15-20 degrees.  Figure no shading issues for either system along with clear sky insolation throughout the whole day.  I'd think that the due south system would put out more solar kWhs over the course of the year.  What would you estimate the percentage difference to be, on a yearly basis, between these two systems?

marco
ProVision Technologies
Hilo, Hawai'i


These are orientation multipliers for the two states

For New York:

Direct./ oTilt	0o	15o	30o	45o	60o	90o
South			0.87	0.96	1.00	0.98	0.92	0.66
SE,SW			0.87	0.93	0.94	0.91	0.85	0.62
E,W			0.87	0.85	0.81	0.74	0.67	0.49


For California:

Direct./ oTilt	0o	15o	30o	45o	60o	90o
South			0.89	0.97	1.00	0.97	0.89	0.58
SSE,SSW		0.89	0.97	0.99	0.96	0.88	0.59
SE, SW		0.89	0.95	0.96	0.93	0.85	0.60
ESE,WSW		0.89	0.92	0.91	0.87	0.79	0.57
E, W			0.89	0.88	0.84	0.78	0.70	0.52

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list