I'm not sure how the 230v 50hz versions operate.  I know that when the US
version of the SW is not synced to the AC source (anytime the "AC1(2) IN
GOOD" light flashing), the reading on the SW's meter goes up then comes back
down at a very predictable rate.  The first time I saw it happen I was a
little shocked but I've since noticed that every SW I've installed does it. 
I always assumed it was taking voltage samples at some point on the sine
wave then displaying that voltage sample (stupid design, yes) and that as
long as the RMS voltage stayed within the window there was no problem with
the unit hooking back up to the grid.

But, you say that yours isn't connecting back to the grid.  Still, it might
not be a problem with the inverter.  I assume that you observed the system
while the voltage approached then reached the LBX transfer point and it
didn't transfer back to the grid?  How long did you wait?  If the loads are
light it might take hours. I fiddled with LBX on several units but it was
always a problem getting to work anywhere near where I wanted it to.  LBX
just hasn't proved to be a very useful or easy to implement feature.  If you
switch the inverter back to FLOAT mode does it hook back up to the grid in
the usual minute or so?


Travis Creswell
Ozark Energy Services



----------
>From: "Carl Emerson, Free Power Ltd." <freepower at freepower.co.nz>
>To: RE-wrenches at topica.com
>Subject: Re: SW fault [RE-wrenches]
>Date: Sat, May 11, 2002, 12:34 AM
>

>Hi there,
>
>I was out at a site today that has been in flawless service as a 'stand alone'
>for about 5 years.
>
>The client has just had the grid connected and I programmed the SW for LBX mode.
>
>When I tested the LBX cutting in I noticed the AC1 meter reading was 'hunting'
>over a wide AC voltage range and not reading the grid volts correctly. It was
>cycling continually from 175 to 260 volts on a 240 volt system.
>
>Because of this the SW failed to synchronize with the grid and refused to come
>on charge.
>
>Is this a common fault ?
>
>I noticed the AC2 was also 'hunting' and not giving a stable reading of the
>generators output. We managed to bet the generator to sync. so that saved the
>embarrassment of a flat bank.
>
>I would be interested to know what causes this fault if anyone knows.
>
>Thanks
>
>Carl Emerson
>
>- - - -
>To send a message: RE-wrenches at topica.com
>
>Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
>
>List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
>
>Check out participant bios: www.mrsharkey.com/wrenches/index.html
>
>Hosted by Home Power magazine
>
>Moderator: michael.welch at homepower.com
>
>

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================





More information about the RE-wrenches mailing list