Trace C60 Rating [RE-wrenches]
jeff.oldham at realgoods.com
jeff.oldham at realgoods.com
Thu Apr 18 15:34:25 PDT 2002
This was not really a derate, but instead U.L. wanted them to handle a
"cloud edge effect" increase in amps of 50% (just as we are required to
design all conductors and over current protection at 156%). In my experience
the C-40 is much more robust than the C-60...
> From the Solar, Wind & Hydro Powered office of:
> Jeff Oldham
> Gaiam- Real Goods & Jade Mountain
> Design & Consulting Group
> 11755 Mid. Mtn. Rd.
> Potter Valley, CA 95469 USA
>
> Ph: 303.222.3814
> Fax: 707.743.1820
>
> www.solardevelopment.com
>
> "When you turn to face the Sun all shadows fall behind you"
> - Old African Proverb
>
-----Original Message-----
From: Lawrence Elliott [mailto:larry at energyoutfitters.com]
Sent: Thursday, April 18, 2002 3:18 PM
To: RE-wrenches at topica.com
Subject: Re: Trace C60 Rating [RE-wrenches]
Bill. I seem to recall when the C40 was just being introduced , someone
from Trace's engineering staff telling me that the C40 was actually
rated to handle up to 63 amps but derated to 40 to comply with UL.
I have two on a hydro as dump loads that regularly see sustained 50 +.
Don't recall who the person was.
Larry Elliott
>
>
>
>
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list