L-16s like higher voltages [RE-wrenches]

hugh piggott hugh.piggott at enterprise.net
Thu Jan 17 00:45:55 PST 2002


<x-flowed>
At 4:59 pm -0700 16/1/02, Ray Walters wrote:
>
>
>2. The report's conclusion that its necessary to EQ at 15.3 v (2.55v/cell)
>for up to 20 hours on a regular basis ( weekly or less) is totally
>impractical offgrid. They mentioned using a generator to do this, but that
>would totally negate any  environmental or cost benefits from going solar
>in the first place.

I am puzzled when I read of this practice too.  It sounds as if some 
people do this.  They use a charge controller to deliberately limit 
the voltage of the batteries when running on solar power (or wind) 
and then burn fossil fuels to wildly overcharge them from time to 
time.  It makes more sense to me to use a higher voltage setting on 
the controller, or no controller at all, if the batteries need more 
charging.  Equalisation should then only be needed as a last resort 
if some cells are getting low.


-- 
Hugh

http://www.scoraigwind.co.uk/

- - - -
To send a message: RE-wrenches at topica.com

Archive of previous messages: http://www.topica.com/lists/RE-wrenches/

List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm

Check out participant bios: www.mrsharkey.com/wrenches/index.html

Hosted by Home Power magazine

Moderator: michael.welch at homepower.com

==^================================================================
This email was sent to: michael.welch at homepower.com

EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com

T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================


</x-flowed>



More information about the RE-wrenches mailing list