L-16s like higher voltages [RE-wrenches]
Ray Walters
remotech at taosnm.com
Wed Jan 16 15:59:50 PST 2002
At 11:23 AM 1/14/02 -0800, you wrote:
>Do you have your customers' charge controller settings for L-16s set too low?
>
>Maybe, check it out:
>
>http://www.sandia.gov/pv/hot/PVQvol_4-2000.pdf
>
>Michael Welch
>
I found 2 major problems with the Sandia study:
1. No where amidst the vast collection of data did I see anything about
Temperature or temperature compensated voltage, so this report doesn't have
me out changing any settings yet.
2. The report's conclusion that its necessary to EQ at 15.3 v (2.55v/cell)
for up to 20 hours on a regular basis ( weekly or less) is totally
impractical offgrid. They mentioned using a generator to do this, but that
would totally negate any environmental or cost benefits from going solar
in the first place.
My conclusion:
Sandia Labs should do a cost benefit analysis of shortened battery life and
lost capacity versus total operating costs for small generators (3kw to 20
kw). I think the cost of running a generator 600 to 1000 hours a year would
be far greater than replacing L16s slightly more often. Also, my
experience is that batteries go bad in the real world because of abuse:
going dry, sitting for months without being fully charged, freezing, or
being contaminated with dirt and baking soda residue.
Solar Ray
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list