Christopher Freitas wrote> The DC-GFP is intended to prevent fires due
to
> the hazard of arcs and overheated conduction paths (that might not
have
> been designed to actually carry power - such as metal roofing or other
> wiring).
Anybody have any knowledge of what the requirements are, and what the
practicalities are for grounding of metal roofs? If arrays are mounted
to existing metal roofs (not anybody's favorite mount I would imagine,
except UniSolar) what would be the best method for grounding the pans if
required?
If the pans were not grounded and a hot wire was in contact with the
roof, how would the GFP trip?
Jason Fisher
Aurora Energy
-----Original Message-----
From: Christopher Freitas - OutBack Power
[mailto:cfreitas at outbackpower.com]
Sent: Friday, January 11, 2002 6:20 PM
To: RE-wrenches at topica.com
Subject: RE: DC GFCI [RE-wrenches]
The DC-GFP is intended to prevent fires due to the hazard of arcs and
overheated conduction paths (that might not have been designed to
actually carry power - such as metal roofing or other wiring).
The real hazard from a ground fault is not necessarily from the PV
panels but from the stored energy in the battery and/or capacitors in
the inverter. The DC-GFP system will limit the amount of fault current
that flows from the battery / inverter when the ground fault occurs.
In most DC-GFP systems the PV array is disconnected in case the fault
was caused by a problem at the PV array. The DC-GFP will actually trip
due to faults anywhere in the system - and will respond to both DC and
AC ground faults as well. By switching the system from a low impendance
to high impedance negative to grounding system connection, the fault
current is reduced to essentially zero.
On a system with two negative to ground connections the DC-GFP would
trip once the system is fired up (no pun intended). This is probably
the best reason for including a GFP - it tells you when you finished the
installation that there is not a ground fault. I was surprised when we
first started shipping GFPs how many calls we got from people saying
"the GFP must be broken - it won't stay on" which of course were
actually caused by having swapped wires or multiple bonding locations on
the DC side.
I think since the cost is so low now ($129 retail for two 60 amp PV
arrays at 12, 24 or 48 vdc) that it is more than reasonable to include a
DC-GFP in nearly all systems, roof mounted or not. The added benifit
of knowing when something is not right is worth it in my opinion.
BTW - I have seen on more than one occasion installations where the DC
system was carrying AC current due to ground faults from bad
transformers inside an inverter or incorrect system design. The DC-GFP
would have warned them of this very dangerous situation.
Christopher Freitas
OutBack Power Systems, Inc.
cfreitas at outbackpower.com www.outbackpower.com
Tel 360 435 6030 Arlington WA USA
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
- - - -
To send a message: RE-wrenches at topica.com
Archive of previous messages: http://www.topica.com/lists/RE-wrenches/
List rules & etiquette: http://www.mrsharkey.com/wrenches/etiquete.htm
Check out participant bios: www.mrsharkey.com/wrenches/index.html
Hosted by Home Power magazine
Moderator: michael.welch at homepower.com
==^================================================================
This email was sent to: michael.welch at homepower.com
EASY UNSUBSCRIBE click here: http://topica.com/u/?bz8Qcs.bz9JC9
Or send an email to: RE-wrenches-unsubscribe at topica.com
T O P I C A -- Register now to manage your mail!
http://www.topica.com/partner/tag02/register
==^================================================================
More information about the RE-wrenches
mailing list